Neither the owner's manual nor the installation instructions list the wattage consumed by the all-electric version of this W/D unit. However, the installation instructions do cite the electrical requirements as follows: "This appliance must be connected to an individual branch circuit, protected by the required time-delay fuses or circuit breakers. A four or three-wire, single phase, 120/240V or 120/208V, 60Hz, 30 amp circuit is required." All properly grounded, of course.
Sorry, there was a problem. Please try again later.Its sad that GE has not answered this question for past 7 years. WATTAGE is not mentioned in GE Website also. They mentioned only 30 Amps, does it mean it will consume Max 240 V X 30 Amp = 7200 Watts at its peak performance. And if we use 120 V then what happens? Will Washer and dryer both work together? GE should have mentioned maximum and normal Wattage for Washer and Dryer separately and together also.
Sorry, there was a problem. Please try again later.Hi - This is Sue at GE Appliances. Thanks for your interest! GUD27ESSJ Electric Dryer should be connected to an individual, properly-grounded branch circuit with 120/240V or 120/208V single-phase 60 Hz electrical service and should be protected by 30-amp time-delay fuses or circuit breakers KW Rating per voltage (240/208). GUD27GSSJ Gas Dryer should be connected to an individual branch circuit with 120-volt single-phase 60 Hz electrical service and should be protected by 20-amp time-day fuses or circuit breakers. This appliance is equipped with a 4-foot long flexible U.S. listed 20-amp power cord to match a 20-amp receptacle. Note: Gas Rated input 20,000 BTU/HR. We suggest to view the Quick Specs online at the following link: http://products.geappliances.com/MarketingObjectRetrieval/Dispatcher?RequestType=PDF&Name=gud27essjJ_27gssj_c3.pdf - We hope this is helpful. Keep in touch!
Sorry, there was a problem. Please try again later.