1-2 of 2 Answers
Minimum 30 amp but a 40 or 50 amp will work fine.
Sorry, there was a problem. Please try again later.Hi Robert2126- Minimum recommended dedicated circuit protection at 208V/240V is 30AMP (KW Rating at 208V =5.1; KW Rating at 240V = 6.8). We encourage you to view the Installation Instructions at the following link - ELECTRICAL REQUIREMENTS: https://products.geappliances.com/MarketingObjectRetrieval/Dispatcher?RequestType=PDF&Name=31-11109-1.pdf - Thanks for choosing GE! SUE@GEA
Sorry, there was a problem. Please try again later.