1-3 of 3 Answers
When the fridge is kicking in it likely is triggering the battery backup. So it's working as designed.. I noticed the same when I had a power drill on the same circuit and it would click when I ran the drill. Should be okay but may also not be fully charging the battery.
Sorry, there was a problem. Please try again later.It's possible click you might be hearing is the battery backup engaging when the normal electric is disrupted. Call the manufacturer to see if they can help.
Sorry, there was a problem. Please try again later.Thank your inquire on our BN650M1. It sounds like the UPS may be going to battery temporarily because of the incoming power. I recommend adjusting the sensitivity on the UPS. To do this you would first turn off the UPS while connected to a wall outlet. Press and hold the ON/OFF button for 10 seconds. The POWER button will alternate green-red to indicate that the Back-UPS is in Program mode. The POWER button will flash either green, amber, or red to indicate the current sensitivity level. I would drop it down to low which would have a green LED. Please do not hesitate to contact an APCbySchneider support team if you need any further assistance. We offer email and chat services through our support site and you may also contact us directly at 800-800-4272 option 4.