I would assume it depends on the hookup in your house. They make different receptacles so it doesnt pay to have one attached already to the unit if it doesnt fit.
Sorry, there was a problem. Please try again later.hank you for your inquiry. The grounding and wiring for the LG 7.4 cu. ft. Ultra Large Capacity Smart wi-fi Enabled Electric Dryer, Model # DKE3500W, like all our Electric Dryers, must conform to the latest edition of the National Electrical Code, ANSI/NFPA 70 and to all applicable local regulations. It has its own terminal block that must be connected to a separate (dedicated) 240 VAC, 60-Hertz single-phase circuit fused at 30 amperes. You can use a 30-amp, 240-volt, 3-wire or 4-wire, UL-listed power cord with #10 AWG-minimum copper conductor and closed loop or forked terminals with upturned ends. A 4-wire connection is required for all mobile and manufactured home installations, as well as all new construction after January 1, 1996. A 3-wire connection is NOT permitted on new construction after January 1, 1996. If in doubt, you will need to check your local building codes or consult your local building inspector about which connection is allowed in your building or home. ^CP