Hi Nick, Thank you for your question regarding the Samsung Wall Oven. This wall oven has a power rating of 10.6 kW at 240 volts and 8.0 kW at 208 volts. The recommended breaker size is 50 amps for a 240V connection and 40 amps for a 208V connection. For wiring, it is advised to use 8-gauge solid copper wire. In terms of amperage draw, the oven pulls approximately 44.17 amps at 240 volts and about 38.46 amps at 208 volts. The recommended breaker sizes provide the necessary overhead to ensure safe and reliable operation. Leo