This is rated at 15 Amp. A 20amp receptacle will have a horizontal bar through the neutral,or long side of the female plug...
Sorry, there was a problem. Please try again later.15 amps. The NEMA configuration is a 5-15. However just because the face is a 15 Amp configuration it is still legal with code to install this device on a 20 Amp circuit such as a kitchen or dining room.
Sorry, there was a problem. Please try again later.15 amp
Sorry, there was a problem. Please try again later.It's a 2.4 Amp @ 5 Volts output (approx. 12 Watts). Should fully charge an iPhone in about 1 hour.
Sorry, there was a problem. Please try again later.Based on the layout of the prongs, it's for connected devices no greater than 15amp. That is not the same as saying whether it can be used on a 20 amp circuit.