1-3 of 3 Answers
You need a 50 amp circuit breaker
Sorry, there was a problem. Please try again later.The LG 6.3 cu. ft. Capacity Electric Single Oven Range with True Convection and EasyClean™, Model # LRE3082ST must be installed and grounded on a branch circuit by a qualified technician in accordance with the National Electrical code ANSI/NFPA NO. 70 - latest edition. All wiring should conform to Local and NEC codes and regulations. Some local codes do not allow grounding through the neutral wire so it will require a 4-conductor UL listed range cord or 4 wire conduit connection. Check with your building codes on what you should use. This range requires a single-phase, 3 wire, A.C 120/208V or 120/240V 60Hz electrical system. A range cord rated at 40 amps with 120/240 minimum volt range is required. If a 50 amp range cord is used, it should be marked for use with 13/8” diameter connection openings. This appliance may be connected by means of conduit or power cord...^IFV
Sorry, there was a problem. Please try again later.I have it on a 220V 20 amp breaker at this time.
Sorry, there was a problem. Please try again later.