1-5 of 5 Answers
Hi java, this Maytag - 7.0 Cu. Ft. 11-Cycle Electric Dryer is manufactured ready to install with a 3-wire electrical supply connection. The neutral ground wire is permanently connected to the neutral conductor (white wire) within the dryer. If the dryer is installed with a 4-wire electrical supply connection, the neutral ground wire must be removed from the external ground connector screw (green screw), and secured under the neutral terminal (center or white wire) of the terminal block. When the neutral ground wire is secured under the neutral terminal (center or white wire) of the terminal block, the dryer cabinet is isolated from the neutral conductor. ■ A 4-wire power supply connection must be used when the dryer is installed in a location where grounding through the neutral conductor is prohibited. Grounding through the neutral is prohibited for (1) new branch-circuit installations, (2) mobile homes, (3) recreational vehicles, and (4) areas where local codes prohibit grounding through the neutral conductors.
Sorry, there was a problem. Please try again later.You will need a new cord.
Sorry, there was a problem. Please try again later.Yes, and if your outlet is old range outlet with three straight prongs, you will need to replace at your expense.
Sorry, there was a problem. Please try again later.Will not install unless new cord purchased.
Sorry, there was a problem. Please try again later.Yes you have to purchase a new electrical cord. If you are replacing a unit, do it right. They are making sure everything is up to date for your safety.