1-2 of 2 Answers
Yes, a single 240 outlet. The breaker switch also needs to be a 50amp breaker
Sorry, there was a problem. Please try again later.Its power requirements are: 120 / 240 VAC, 120 / 208 VAC. This wall oven must be electrically grounded in accordance with local codes or, in their absence, with the National Electrical Code ANSI/NFPA No.70- latest edition in United States, or with CSA Standard C22.1-1982 and C22.2 No.01982 (or latest edition), Canadian Electrical Code, Part1, and all local codes and ordinances. This wall oven must be supplied with the proper voltage and frequency, and connected to an individual, properly grounded branch circuit, protected by a circuit breaker or fuse. For the circuit breaker or fuse required by this model, see the rating plate to find the wattage consumption and refer to the table below to get the circuit breaker or fuse amperage. • A Microwave Combination Wall Oven can consume up to 7,800 W at 240 VAC. A 50 Amp circuit breaker with wire gauge #8 AWG must be used. • Do Not ground to a gas pipe. • Do Not have a fuse in the neutral or grounding circuit. • A U.L.-listed conduit connector must be provided at the junction box If you have additional questions, you can contact our Customer Support by any of the below options: Phone: 1-800-243-0000 LiveChat: https://www.lg.com/us/support/chatbot Email: https://www.lg.com/us/support/email-appointment Facebook Messenger: https://www.facebook.com/LGUSA/ Twitter DM: @LGUS The LG Community Forum is also a great resource for getting help from other LG customers: https://lgcommunity.us.com/ ^CP