The reason that the power cord does not come with the LG 6.7 cu. ft. Capacity Electric Double Oven Range with Infrared Grill and EasyClean™, Model # LDE3037ST is because Double Oven Electric Convection Ranges that have an amp rating of 40 amps, 208/240V rating when installed in Mobile Homes, recreational vehicles and in installations where local codes do not allow grounding through the neutral wire will require a 4-conductor UL listed range cord or 4 wire conduit connection as dictated for new branch-circuit installations (1996 NEC) This appliance must be installed and grounded on a branch circuit by a qualified technician in accordance with the latest edition of the National Electrical Code ANSI/NFPA No.70. You may happen to live in a building that requires a 3 Wire receptacle (10-50R) as you will find in many older buildings or maybe one that requires a 4 Wire receptacle (14-50R), as required for new buildings and constructions after Jan 01 1996. All wiring should conform to Local and NEC codes,and that ultimately will determine which cord you need to get for the appliance...^IFV
Sorry, there was a problem. Please try again later.There are different 220/230 volt receptacles, not knowing which is in service where the range will be used; therfore supplying every configuration of cord available becomes impractical.